Hello All,

I have analyzed a fink truss (2x4 TC, 2x4 BC, 1x6 Webs (nailed) & plywood Gusset) that has had some substantial foam encased HVAC duct work hung from it. I am analyzing it to see if there might be a way that I can get some additional capacity out of it, but it appears that with my conservative values for the snow load, wind load, and HVAC loads the TC and BC are above 1.0 stress index!

I'm thinking that the BC is fine because there is a living space below with walls bracing it, but the TC is my issue!

Other than sistering the TC with new lumber, any other tricks you folks have found. I'm looking to strengthen it to get another 5-6psf out of it.

Thanks all

RE: Ideas to Get additional capacity out of Fink Truss

Brother the top chord.

Mike McCann
MMC Engineering

RE: Ideas to Get additional capacity out of Fink Truss

... or you could sheath one entire side in plywood, and around the ducting.

Mike McCann
MMC Engineering

RE: Ideas to Get additional capacity out of Fink Truss

If there are interior walls bracing the bottom chord (I assume you mean support - intentional or un-intentional), then the top chord axial load is lessened as well.

RE: Ideas to Get additional capacity out of Fink Truss

(OP)
Sorry. Supported, yes. Long day yesterday!

RE: Ideas to Get additional capacity out of Fink Truss

mquared48,

A quick pedantic question if I may. I'm familiar with the term "sistering" and I and use it when describing how to strengthen a wood joist, i.e., "sister" a new member to the existing member. Is "brothering" another way to say the same thing, or does it mean something different? Thanks.

RE: Ideas to Get additional capacity out of Fink Truss

That is when it is sistered, but not too well bigsmile

RE: Ideas to Get additional capacity out of Fink Truss

Yeah, I'm pretty sure that "brothering" was an attempt at humor ;)

Either that or I'm about to learn something new...

RE: Ideas to Get additional capacity out of Fink Truss

What is the span and the roof pitch? Is the bottom chord fully supported or is it open? I'm guessing the 2x6 webs are in order to reduce lateral bracing requirements on the webs.

I think you might see some benefit from a more rigorous analysis. Your conservative estimates might be what's killing you. For example, none of the load cases require 100% snow + 100% wind or 100% live + 100% snow/wind. Attic live loads are not required to be concurrent with other live loads. Are you considering snow load and live load reductions for roof pitch and roof area? Can you discount attic live loads for trusses without a ceiling or pull down stairs? An analysis will tell you what is the weak link. Perhaps it is the connections. Perhaps it is the lateral braced length of the webs or the bottom chord. The solutions to these problems are different.

RE: Ideas to Get additional capacity out of Fink Truss

You sister on the right side, and brother on the left. But that too depends on how you look at it. :)

Mike McCann
MMC Engineering

RE: Ideas to Get additional capacity out of Fink Truss

(OP)
Charlie...

I am actually calculating the actual snow load (based upon ground snow load in our area, and then reducing it for pitch), adding in the DL of sheathing, etc, adding the DL from the HVAC installation and then determining web stresses.

Both the bottom chord and top chord are overstressed, webs seem to be fine. Bottom chord is supported by walls below, so I'm thinking I am ok there. Top chord is my concern, as well as the gusset plate (it is wood) at the heels.
http://www.eng-tips.com/
I was considering sistering a new TC member (2x4) glues and screwed to existing member, and then adding an additional heel gusset plate.

Thanks again for the help.

RE: Ideas to Get additional capacity out of Fink Truss

Is the TC failing mainly in compression or bending?

RE: Ideas to Get additional capacity out of Fink Truss

(OP)
Bending. Buckling seems to be ok.

RE: Ideas to Get additional capacity out of Fink Truss

is the ductwork hanging from the top chord?

RE: Ideas to Get additional capacity out of Fink Truss

(OP)
YEs, hanging from the top chord, but not even tied to every truss member, about every other or every three.

There is also four laterals running on each side that is fairly rigid and only supported from the mail trunk and at the drywall ceiling as it enters the ceiling below.

RE: Ideas to Get additional capacity out of Fink Truss

sounds like sistering may be the best option

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources