Working with a new client who has been installing handrail posts with a 1 1/2" edge distance for years. As the new engineer they need me to create calculations for their shop drawings. I can't get the calculation to work for a 6" deep embedment into the concrete. They typically have the following criteria: Fc'=2500psi (sidewalks) Post Spacing=5'-3"
I resolved the moment at the base of the post using a 4" T-C couple in the embedment. That seems as a reasonable pressure resolution of forces. I end up with 2.7k unfactored. Adding in the 1.6 factor to 4.4k. If I do just a straight shear calculation in a shear plane and just forget about appendix D for a sec,. I only get around 1000#,. I got around 385# using appedix D if I don't avoid D.3.3.6,. how have any of you got this to work? What am I missing? any and all help is much appreciated. Thanks!
RE: Handrail Post Embedment Edge Of Slab
If it has to be to current code you won't ever get it to work with Appendix D for just 1 1/2".
Can you use a #3 hairpin and resolve the force couple by developing the rebar? That is your only hope, OB1, with that tight of edge.
www.FerrellEngineering.com
Providing fabrication and erection efficient structural design of connections. Consulting services for structural welding and bolting.
If the slab is existing, you have my sympathies... But could you possibly core drill through the sidewalk and underpin underneath with a new footing for the handrail, not depending at all on the sidewalk?