single core AC cables termination

single core AC cables termination

single core AC cables termination

(OP)
We are installing a 160kW VSD in a substation. I notice that contractors have routed the 6 single core flexible cables to the VSD through a steel gland plate. To my knowledge this is a NO NO because of inductance and eddy currents.
any Comments?
PS For such installations what size should the earth cable be? Minimum 50% of main conductor size is my guess?

RE: single core AC cables termination

I agree that that is not good practice, although it may be allowed under Canadian code depending on the current. The Canadian code prohibits the entry of a single conductor through a ferrous plate when the current in the conductor is greater than 200 Amps. At 380 Volts or 480 Volts the current in the individual conductors will be below 200 Amps.
And notwithstanding single conductor cables may enter a ferrous plate if the plate is properly slotted so that each group of three holes is effectively one hole and non-ferrous gland connectors and locknuts are used.. If conducting plates are used at each end of the cable run, provision must be made to interrupt sheath and/or armour currents or the cables must be de-rated.
Note: These are code requirements under the Canadian code. Your codes may differ.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources