Hi can any one help pls.
I have mv cb provided by oc/ef relay supplying dist transformer.
When main feeder trip this cb also trip for information this yransformer on seprate feeder but from one main sustation.
Thank you
I have mv cb provided by oc/ef relay supplying dist transformer.
When main feeder trip this cb also trip for information this yransformer on seprate feeder but from one main sustation.
Thank you






RE: pls help for this
WHAT was the question?
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: pls help for this
I have RMU switchgear connected to transformer 500 kva (package sustation)
And this substation getting supply from main distrbution feeder 11 kv
My question :
When some feeder from the grid station trip the package substation CB trip?
Why the circuit breaker which connected to transformer trip due to other main feeder trip?
I hope my quiestion is clear.
Thanx all.
RE: pls help for this
when feeder 1 trip the transformer 500 kva trip also.
RE: pls help for this
Is there any targets ?
RE: pls help for this
no the device which installed over current and earth fault only .
and the transformer load almost 90 % of nominal capacity .
RE: pls help for this
What type of relay is installed, what settings of overcurrent and earth fault.
what Uk of transformer? and what type of load on the transformer ?( maybe motors).