Help!!!!!!! Bull head side of tee looking up or dn
RE: Help!!!!!!! Bull head side of tee looking up or dn
Which tee exactly? The one in the centre?
Based on the others I'd guess up, but you shouldn't have to guess.
Thanks for help!
David Simpson, PE
MuleShoe Engineering
"Belief" is the acceptance of an hypotheses in the absence of data.
"Prejudice" is having an opinion not supported by the preponderance of the data.
"Knowledge" is only found through the accumulation and analysis of data.
The plural of anecdote is not "data"
What does this mean?? "Normally open" ???
You have 4x tees, the discharge branches of all four of the 4x tees are "up" in your plan view, hidden line dwg.
You also have two more problems:
1. Unless there is an elevation view to this pipe rack, your draftsman failed to specify how far "up" the the branch rises on the nbr 4 tee running to the right side before it goes back back down to its remaining horizontal run.
2. Your draftsman/checker/designer failed to specify how far "up" the vertical run (the pipe going to the cutoff valve blocking the "future run" of pipe coming out of the valve) is to be, what the height the center of the blocking valve is to be, and where the operator of that valve is to stand when he needs to open or close that valve. Looks like a butt-welded valve is the only thing possible per the sketch, but that allowed/required in the piping spec's for these lines?