We have an abb 266hsh and the sensor span limits are 0.65 and 65kPa. am i correct in assuming that our calibrated range of -10 to 10 kPa will be fine for this transmitter as it falls within these limits?
thanks

RE: Pressure transmitter span limits

Yes. The spec sheet gives the range as -65kPa to +65kPa with a minimum span of 0.65kPa.

Your range of -10 to +10kPa exceeds the minimum span and falls within the stated range.