after calibration my electric meter is still innacurate. the contractor says the current transformer(CT)is incorrect. mine was used for control and not for metering, the reasons its innacurate. is this possible? how many types of CT are in the market? what type is use for electric metering?

RE: CT(current transformer) rated electric meter

Generally metering CTs are more accurate than protection CTs (especialy at the lower values of current) but saturate at much lower currents. I'm responsible for a good few tariff metering circuits (UK based) that range from around 5MVA to 700MVA and most of those use class 0.2s CTs, some of the smaller circuits have class 0.5s. I've seen VTs that have protection and metering ratings but not CTs.

RE: CT(current transformer) rated electric meter

Well, maybe, yes, many, it depends, possibly not: If you want a reasonable answer then include some pertinent data.
Sizes?, secondary current?, calibration?, burden (rated and actual)?, at what PU of rated load do you see inaccuracy?, What are you using the measurement for?
A measurement class CT should be accurate to around 200% of rated current. A protection class CT may be inaccurate at low current but will not saturate until a much higher current than a metering class CT.
If you are attempting to determine the kW of a load with a significant inductive or capacitive component with voltage and current alone, then Google "Power factor".

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources