I have a connection where I would like to install an anchor(s) in the top of a concrete slab. The anchor(s) will need to take a shear load but no tension force. The issue I'm running into is the slab has a total thickness of 3" and is supported by 9/16" non-composite metal decking. Additionally the bottom of the slab is not accessible for any kind of a thru-bolt connection.

Are there any mechanical or adhesive anchors that can be installed in a slab that thin?

Would the use of a masonry anchor be acceptable? (i.e. Hilti HY20 with a screen)

RE: Minimum Embedment for Anchor in Concrete?

So you have a non-structural form deck with a total of 3" maximum thickness of concrete cover, therefore only about 2.45" of concrete to play with.

I would check the Hilti Profus program that is compliant with Appendix D using your loads and see what pops out.

Mike McCann
MMC Engineering

RE: Minimum Embedment for Anchor in Concrete?

(OP)
Looking at the anchors in Profis and also the Simpson anchors neither gives me an option for concrete that thin. That's where I started considering the use of a masonry anchor with a screen.

RE: Minimum Embedment for Anchor in Concrete?

Shear loads are generally transferred to the anchor in the form of tension. I'd talk to the Hilti engineer to see what anchorage is possible. The use of the screen is a definite possibility.

Dik

RE: Minimum Embedment for Anchor in Concrete?

There was a thread about this last week. Try the Hilti program and see what it comes up with. Good program.

RE: Minimum Embedment for Anchor in Concrete?

What about drilling through the slab, inserting a toggle bolt, and epoxying in the excess diameter of the hole??

Mike McCann
MMC Engineering

RE: Minimum Embedment for Anchor in Concrete?

Try contacting Hilti. A local Hilti field engineer helped me in the past with anchors in 2-1/2" Light Weight Concrete on 1-1/2" deck (4"total).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources