Hello Engrs
We conducted a tan delta test on a 30MVA, 132/33KV transformer recently using OMICRON CPC 100. At different voltages we had values like -6%, 0.5 % and 23%. What can we deduce from these. Iread that for good insulation the value should be around 0.007%
what does the minus sign imply.
We conducted a tan delta test on a 30MVA, 132/33KV transformer recently using OMICRON CPC 100. At different voltages we had values like -6%, 0.5 % and 23%. What can we deduce from these. Iread that for good insulation the value should be around 0.007%
what does the minus sign imply.






RE: tan delta
Lots of moisture *could* be a reason. But those numbers are all over the place and indicate bad measurement practice. Or faulty equipment.