WWTP Expansion Joint Detail

WWTP Expansion Joint Detail

WWTP Expansion Joint Detail

(OP)
We're in the final stages of submittal for a wastewater treatment plant. The tank on the plant was large enough (around 200' x 100') that adding an expansion joint seemed prudent. Our detail for the expansion joint is attached, as this is our first time designing a tank this size, I'd love some feedback on any possible problems with it.

https://www.dropbox.com/s/z1mg8n7kod67eb5/expansio...

Thanks

Brian C Potter, PE
Simple Supports - The history and practice of structural engineering.
ConstructionPic - Send annotated jobsite photos.

RE: WWTP Expansion Joint Detail

I can't open your link. You need to attach it in a different way or my company's spam filters will block it. Try the attachment block.

RE: WWTP Expansion Joint Detail

First of all, I'd go with profile 738 from greenstreak. You don't want the 3/8 to 1/4 taper and that thin centerbulb might tear. I'm not a believer in the smooth dowels. It's unlikely they're going to do much good if you get significant movement. Some peolpe like them, so to each their own.
The Cadillac of sealants is Sikaflex 2c. I'm not sure what Sika Tank is, but the sealant can make or break an EJ. It's the only visible part, so if it tears, you're going to hear about it. You'll need to shape the sealant and use a bond breaker. Pay attention to all the Sika sealant literature. Ignore it at your own risk. Bond breakers and rubber fillers seem unimportant, until you've ahd a couple of hundred feet of sealant ripped out and your boss has to pay for it.

RE: WWTP Expansion Joint Detail

My personal preference is for an external water bar, rather than a central bulb type.

Also, is you dowel bar capped for half it's length? The diagram seems to show the cap less than this?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources