CMU grout spacing
3

CMU grout spacing

CMU grout spacing

(OP)
I have a project where the footing rebar was bent over into the incorrect cell for a CMU wall. For instance, the wall is specified to be grouted at 24" on center but is actually 16" one direction and 32" the other. Do you have any opinions on this or sources to review before directing corrective action?

RE: CMU grout spacing

Is grouting required at 24" o.c. for structural purposes?

RE: CMU grout spacing

Is it cantilevered or a wall that spans b/w roof and foundation?

RE: CMU grout spacing

(OP)
It is a wall that spans between a footing and roof structure. It is load bearing so grouting is required.

RE: CMU grout spacing

But is grouting at 24" required or is 32" sufficient. If you finessed your loads you might find that at 32" the wall is fine.

RE: CMU grout spacing

It sounds like a missed communication between the footing drawings and wall design, since the bars are already there. - Sometimes a quick look back on the loads and assumptions could be valuable, hence the lateral load distributions can vary. Were different engineers involved in the footing and wall designs?

A possibility is using a different f'm for the masonry strength since it is very common for that to be 50% or more greater than is commonly assumed

Dick

Engineer and international traveler interested in construction techniques, problems and proper design.

RE: CMU grout spacing

Being a simple span wall, there's likely no stress on that bar coming out of the footing anyway. If it were me, I'd grout the (wrong) cell with the bar above the top of the bar just to utilize is for shear connection b/w wall and footing. Then add a continuous bar in the adjacent, correct cell and work my way up from there. Maybe throw a 180° hook on it if I'm development issues with the embed...but that is unlikely.

RE: CMU grout spacing

As azcats suggested, you can always add a bar that isn't lapped to the dowel to assist with out of wall plane bending at the spacing you need. A straight bar will be developed at mispan for a typical 10'-0" wall height. You have your footing dowels as needed for shear transfer.. done and done.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources