Low voltage control cables
Low voltage control cables
(OP)
Do LV control cables have to be shielded? What is the downside if these are not shielded?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Low voltage control cables
|
RE: Low voltage control cables
RE: Low voltage control cables
There is no code or rule that says they need shielding, it depends on the application.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
RE: Low voltage control cables
The spec states the below,
LV Control cable shall be 0.6/1kV grade, and have stranded annealed copper
conductors of at least 1.5 sq. mm size, extruded PVC Insulated, extruded FRLS
PVC outer sheathed. Control cables shall be screened and grounded to eliminate
any spurious voltage pick-up. Cable shall comply with IEC 60754 Part-2.
RE: Low voltage control cables
Test on gases evolved during combustion of materials from cables -
RE: Low voltage control cables
My friends on oil rigs also like to see external armor braid to protect the insulation and shield from falling wrenches and such.
Mike Halloran
Pembroke Pines, FL, USA
RE: Low voltage control cables
Interesting that the specifier used the IEC term screened instead of shielded, but then used "grounded", a typically ANSI term, instead of "earthed". Or in IEC terminology, does grounded mean something different from earthed?