I have a question regarding a ground application on a delta system. We bought a High Resistance Grounding system. We had a choice for a Wye(broken)-Delta or Zig-Zag transformer to create the neutral point. We chose the Zig-Zag for the added benefit of harmonics.

When we receive the unit we found that the manufacture uses 3 individual single phase transformer for the zig-zag circuit. An issue that was brought up that is above my knowledge level is a concern that the unit will not operate properly because (bare with me) something to do with the Flux resistance/impedance through the air because of the single phase transformers. The proper application 3 phase zig zag transformer with common iron core and not three single phase transformers.

I hope someone can shine some light on the subject.

RE: Zig Zag Transformer

I'm guessing that they used single transformers for the outriggers of the zig-zag to get a turns ratio which they couldn't get from a single 3 phase core. I see no reason that these single transformers should have any problems coupling flux from one winding to another. It's all vector addition.

RE: Zig Zag Transformer

I think it is about shell transformer-5 columns 3 phases-which presents less magnetic flux leakage and so a reduced reactance. A usual 3 columns transformer reactance will be not so reduced.

RE: Zig Zag Transformer

A three legged three phase transformer does not have a path for unbalanced flux. This is not an issue with single phase transformers.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Zig Zag Transformer

Three single phase transformers with zig-zag connections should work perfectly well as a three limbed three phase transformer. Since the rating of grounding transformer is so small, 3 phase construction is normal, but I dont find any issue with three single phase transformers with correct connections between windings.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources