Quick disconnect (natural gas service) with proof-of-closure

Quick disconnect (natural gas service) with proof-of-closure

Quick disconnect (natural gas service) with proof-of-closure

(OP)
I am looking for a way to quickly connect/disconnect a 2" or 3" flex hose from an industrial burner. Natural gas supply line, operating pressure 20# / design pressure 100#. Does a quick connect exist that assures no leaks and can prove closed to BMS? Thanks!

RE: Quick disconnect (natural gas service) with proof-of-closure

Check TODO couplings, maybe there is something for You

RE: Quick disconnect (natural gas service) with proof-of-closure

(OP)
Thanks for the response. I spoke to TODO awhile back, but they said it is not for natural gas. I don't need the dry-break system where the coupling seals, as I can vent the line upstream of the coupling. Just need a quick disconnect that will be a sure seal in service.

RE: Quick disconnect (natural gas service) with proof-of-closure

Did you look at WECO unions?

Petrotrim Services
www.petrotrim.com

RE: Quick disconnect (natural gas service) with proof-of-closure

(OP)
I had not. That looks like a good candidate, thanks.

RE: Quick disconnect (natural gas service) with proof-of-closure

3" flex hose is a lot of gas that remains as a hazard inside the hose: Seems to me you want a permanent valve to isolate the nat gas first.
Then, close to that valve outlet, a small air line to purge the pipe and flax hose once isolated.
Then, the pipe running to the flax hose
Then, the flex hose itself
Then the QD flange or fitting.

Sequence: Shut the nat gas supply valve, open the purge line to clear the nat gas out of the line, shut off the purge air, open the QD flange and disconnect the flax hose.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources