Motor Space heater size and terminal box according to NEMA standards
Motor Space heater size and terminal box according to NEMA standards
(OP)
In NEMA 01 is specified that "For machines rated 601 V and higher, accessory leads shall terminate in a terminal box or boxes separate from the machine terminal housing. What about lower than 600V? Is a terminal box required by NEMA for space heater leads? Is there a table with space heater size related to motor size in NEMA standards - it should, but I don't know where to look.





RE: Motor Space heater size and terminal box according to NEMA standards
"Will work for (the memory of) salami"
RE: Motor Space heater size and terminal box according to NEMA standards
One additional thing is to check local and industry requirements. I do recall we had one nuclear safety related 460vac motor located in EQ harsh environment where plant licensing documents specifically required space heater and rtd leads routed through separate terminal box from main leads I can't phathom the original technical basis for that requirement, but as we investigated we found it was not something we could deviate from and we ended up doing a lot of rework to get our replacement motor to conform to the requirement.
=====================================
(2B)+(2B)' ?
RE: Motor Space heater size and terminal box according to NEMA standards
Muthu
www.edison.co.in
RE: Motor Space heater size and terminal box according to NEMA standards
Nice to hear from you - seems like you've been away for a while.
Regards,
dpc
RE: Motor Space heater size and terminal box according to NEMA standards
Muthu
www.edison.co.in