(OP)
"Comply with standard specifications for billet bars for concrete reinforcement ASTM A15-54T".

Am I to assume fy of 33 ksi or 40 ksi?

RE: Reinf. note on drawings from 1961.

I believe that standard came in a variety of grades: structural, intermediate, and hard. The yield stresses would have been assumed to be 33, 40, or 50. Do you see any notes designating the grade?

The A15 standard also could have been for smooth bars or deformed bars depending on the era so you should confirm they are deformed.

RE: Reinf. note on drawings from 1961.

(OP)
jd, the only relevant note I can see is "for deformation of reinforcement comply with ASTM A-305-50T". Other then they have a note for column reinforcement as "ASTM A16-54T"

RE: Reinf. note on drawings from 1961.

(OP)
Slide, I found the same result that you posted with my google search but did not find it conclusive. My notes do not say anything about intermediate etc.

RE: Reinf. note on drawings from 1961.

I've only worked on a handful of retrofits of buildings during that era so I'm not sure what was most common. The reinforcing on those projects I believe was all specified as intermediate. I don't know if that is typical for most buildings or not. Perhaps, someone with more experience during that time can chime in if certain bar sizes came in certain grades more commonly. Personally, I'd just assumed fy = 33 ksi unless you have reason to suspect otherwise.

Depending on the work you are doing, it probably also is a good idea to take some steel coupons of the reinforcing to confirm properties. ASCE 41 has recommendations on how many coupons to take, etc.

RE: Reinf. note on drawings from 1961.

(OP)
Thanks jdg, I was leaning towards the safer side (33 ksi) and I'll go with that for now. Would recommend field testing if the retrofit solution gets too elaborate.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources