Tightening Anchor Bolts with torque wrench
Please, I need urgently check the tension of A325 anchor bolts. The bolts are supposed to be tensioned to 20 and 30 kips. The torque wrench to check the bolts shows the values in ft-lbs.
What value in ft-lbs at the torque wrench corresponds to 20 kips and 30 kips? Thanks any objective and straight forward reply
RE: Tightening Anchor Bolts with torque wrench
1. What diameter is the A325 anchor bolt you are trying to tighten?
2. Are you sure - absolutely positive!!!!! - that you are trying to get to 25,000 lbs force on that bolt, or did you really want 25,000 psi pre-stress on the bolt?
3. Did you double check (again) where you found the answer to nbr 2? Why do you thik 25,000 lbs force is correct?
4. How long is the anchor bolt penetrating into the slab?
5, What quality concrete have you assumed, and how long has that concrete/rock/gravel been curing?
6. How far apart are the anchor bolts?
7. How far is the closest anchor bolt to an unsupported edge, curb, or expansion joint?
8. How thick is the slab you are drilling into?
9. How are you fastening the anchor bolt into the concrete? (expansion collar, adhesive or epoxy, grout, plate on the end of the anchor bolt, nut on the anchor bolt, bent anchor, smooth anchor bolt or deformed?)
10. Where is your force? Sideways to the surface of concrete, vertical, or a combination of the two?
11. Are the loads on every anchor bolt the same?
Unless you have a really strange spec, there is generally no reason to pre-tension anchor bolts. Anchor bolts are generally tightened to a "snug tight" condition.
Give more info please.
Assuming you meant you are installing a A325 high strength bolt that is required to be pretensioned, there are 3 methods available to pretension: turn of the nut, calibrated torque wrench, and direct tension indicator.
A non-calibrated torque wrench can not be used. It's my understanding that the wrench needs to be calibrated to prove that a certain torque on the wrench provides the required pretensioning value.
Thanks for trying to answer. I need a very simple answer. The minimum tension to verify at the anchor bolts are 20kips and 30 kips. Which values in ft-lbs at click torque wrench makes me feel confident that I have reached the correct minimum tension of tightening.
The bolt are A325 - 5/8" and 3/4" diameter. They are used on prefabricated steel buildings.
Why the high preload?
You can get A325 bolts in a longer format, and they may be specially fabricated. For that sort of load, you should be looking at maybe 16" min embedment to develop the headed bolt.
Dik
Like the others, I haven't seen A325s used for anchor bolts, nor can I think of a reason to pre-torque to those levels.
Michael.
"Science adjusts its views based on what's observed. Faith is the denial of observation so that belief can be preserved." ~ Tim Minchin
Doing purely the maths the torque figures according to me are 7363.3lbft and 4090.66 lbft. These calculations of torque are based on dry fasteners for which I have assumed .2 is the friction factor.
I would add that using torque to preload bolts is highly inaccurate with errors of upto 40%, also the clamping of component parts need to be considered which you give no details of.
Dia. nth Ab Abe Abr Abe/Ab Abr/Ab
5/8" 11 0.3068 0.2260 0.2017 0.7367 0.6576
3.7.1.1 LRFD
An alternative method for the determination of the tensile strength of bolts is
used by the LRFD (AISC, 1994). The capacity is computed as
EQ 3-7
where
Bn = the nominal tensile resistance of the bolt
Ft = the effective tensile strength of the bolt material,
Ab = the nominal area of the bolt’s shank
Ft is taken as 90 ksi for A325 bolts and 113 ksi for A490 bolts. Table 3-4
shows the ratios of the effective tensile area of a bolt to its gross area. Since Abe
/ Ab is approximately equal to 0.75, Equation 3-7 provides a reasonable estimate
of the bolt strength for the range of bolt sizes typically used for bolted connections.
For design, the nominal tensile resistance of the bolt, Bn, is multiplied by a resistance
factor, fbf, of 0.75.
I'll dig up a source. It could be that the various friction surfaced... washer to base metal, nut to washer and thread to thread make it difficult to establish a uniform value for all instances...
Dik
I think I made a mistake in doing the maths, when I rechecked my figures I now get 64 lbFT and 165 lbFT sorry!
http://www.engineersedge.com/calculators/torque_ca...
The above link will help you figure this out, but once again, I would really question the values that you are trying to achieve. As you will note on the site, it makes certain assumptions about friction, so calibrating the wrench would be required.
I think the 100 ft. lb. developed about 20 kips tension. The bolt deserved to pull out. My lesson was not to torque anchor bolts. There is no reason.
And there's no reason to use A325 bolts. These are for high strength steel to steel connections. You torque them to develop frictional resistance or to allow energy to be used during repetitive loadings (like a seismic event).
I'd snug them up. Torqueing them adds no advantage.
Just out of curiousity, was this with an anchor plate on the anchor rod or just an embedded rod?
I think the torqueing loosened the bond at the top of the anchor and it progressed from there.
If this is a process tower and bolt is properly embedded and sleeved you can determine the bolt pretension by the bolt elongation.
There are specialty contractors who will do this type of work without asking "what tork do ya want?
Okay I realise I must be getting old as I read kips as being pounds per square inch, now I realise that its just pounds, using the approximate formula for bolt torque below:-
F= T/(0.2*d)
transpose for T therefore T= 0.2*0.625/12 * 20000 = 208 lbft
for the 3/4" bolt I get 375 lbft.
Having looked into this more, I have to agree with the other posters regarding the snug tight comments and these high preloads not being required.
Still the bottom line is....no need to pre-tension an anchor bolt in a building.
Thanks for your comment,its amazing what one can learn on here, I never realised that a base plate wasn't clamped down till I looked on here for more information, I just assumed that bolted joints always clamped stuff down, but it does mean that any uplift on the base plate is directly transferred to the anchor bolts and that theoretically the base plate may separate from the concrete, that's something we would avoid in mechanical joints.
But a 5/8 dia bolt (even A325) isn't strong enough (as I see the references) to stand that much preload.
18 and 36 ft-lb for 20 ksi
27 and 56 ft-lb for 30 ksi
ASSUMING:
-A coefficient of friction of around 0.12
-Tightening of new, lubricated bolts
The relationship desertfox gave above is reasonably accurate and comports with direct tension testing in a Skidmore-Wilhelm device.
on a side topic.... i'm pretty sure the 'calibrated torque wrench' is an installation wrench calibrated to stop turning gears at the torque that a bolt qualifies in skidmore, and the inspection occurs at the time of bolting to confirm successful procedures used... the clicking torque wrench as an inspection tool is for arbitration when there is no better alternative left, which occurs a lot. i suppose if that wrench were used to install that would work, but once the bolts are in-place, it's arbitration.