Grounding of CT's on a new transformer. Where should the ground connection be located?
Grounding of CT's on a new transformer. Where should the ground connection be located?
(OP)
We got our new oil-filled transformer that came with CT's that are each wired out to terminals on the top of the transformer. From there they are wired to a control panel at ground level.
Looking inside the terminal well of a CT on the top of the transformer, and per the transformer drawing, one side of each CT is grounded up there to the case of the transformer.
If these are left in place it seems it would put these CT's in a 3-phase wye configuration.....Is the intent of this, or is this wrong? We would typically ground the CT's at the control panel. Do you have to ground both sides of a CT when de-energized and performing maintenance?
Looking inside the terminal well of a CT on the top of the transformer, and per the transformer drawing, one side of each CT is grounded up there to the case of the transformer.
If these are left in place it seems it would put these CT's in a 3-phase wye configuration.....Is the intent of this, or is this wrong? We would typically ground the CT's at the control panel. Do you have to ground both sides of a CT when de-energized and performing maintenance?






RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Also, my personal preference is to ground the CT at the equipment from which it originates, though I think there are various practices. I prefer this because it's a logical way to avoid multiple grounds. If your policy is to ground at the originating equipment, you don't have to decide which control panel to ground in.
Another practice would be to ground the CT at the first panel the CT enters once it leaves the equipment from which it originates.
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
This has been discussed previously - you might try searching the forum.
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
The circuit should only be grounded at a single point. Otherwise you may void any neutral current readings your protections might want to use.
If the CT circuit ground is located in the control / relay building, the circuit will be less susceptible to interference from the switchyard.
Where in the relay building you choose to ground the circuit is up to you. It’s a good idea to allow for multiple grounding points via sliding link terminal blocks on the back of the panels the CT circuit is connected to. If you do this there is also a possibility of the CT ground connection being compromised.
Mark
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Sorry if I'm being redundant.
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Instrument transformer secondaries should be connected to ground at only one point (see IEEE Std C57.13.3). Making the ground connection at the relay or control building has the following advantages:
Voltage rise is minimized near the relay equipment.
The shock hazard to personnel in the building is reduced.
All grounds are at one location, facilitating checking.
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
The Vendor did put temporary jumpers to short the terminals at the control panel which were removed so to get the wires to the relays.
I'll post another sketch of the proposed solution.
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Some redesign suggestion.
1. Get rid if the isolating type terminal block, the knife switch. That is an accident waiting for a chance to happen.
3. Exchange the sliding link with Weidmuller presdure type TB snd change the vonnectors with one that has a small bend tab; do not know make and model, but had beeb discussed in this forum in the past.
3. The slide link is OK in a CT junction box for acess by a qualified personnel, but you could install one more for every CT so that you can slide it close to short out the CT winding if required without disturbing existing wiring. CT single point ground then goes in the same box.
note: secondary cct schematic is incomplete and is now open circuited, relay polarity not shown. all info is pertinent for proper review.
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Existing CT grounds to be removed.
CT grounding done by jumpering the CT neutral (X2, looks like single ratio on dwg) to each other then 1 connection to the ground bus.
Polarity may be reversed at the relay, typically X1 (incoming as per dwg) goes to polarity input terminal on relay and sum of ABC also to polarity on ground input terminal at relay.
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Get rid of any terminal that may open the circuit. Open circuited CTs are dangerous and may be lethal.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Are you saying all of these terminals should be replaced with a feed-through style? Also, you are saying all the grounded wires from all three CT's should be jumper-ed together and one wire taken to the ground bus?
Knowing the hazards of an open circuited CT I don't really see how a xfmr mfg has an excuse to supply us with this style of terminal. If there is something else I just learned in this -> specify exactly what you want. You won't get it otherwise!
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
http://www.clrwtr.com/PDF/Weidmuller/Weidmuller-Sc...
https://www.phoenixcontact.com/online/portal/us?ur...
They are intended for CT use but possibly not as they are connected in your drawing.
While it is electrically possible to connect a meter to the test points and then open the shorting link, it may not be safe. A safer use may be to use the shorting feature to short the CT leads. Meter connections may then be changed and the shorting link opened for testing.
Good practice is to complete the wiring of the CTs with the same type of wire for both the CT polarities. Then add one jumper to ground.
Never assume that a ground path has a low impedance and never assume that a ground path will never be inadvertently opened.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
The attached sketch shows what I think you mean. Top is Demo, Bottom is new. The Jumper numbers are J1, J2, etc. for reference.
I don't like the fact these have 3 wires under a terminal. The ground connection for each one can't go straight to the ground bar?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
But looking at these slide type terminals, they don't seem that substantial to me. I wish there was a better way to do this. I certainly hope they don't get used a lot.
Our guys have commented before they don't like the shorting block type terminals either on the CT circuits. They would rather make up their own jumpers and short them to ground.
I haven't seen them do it, just heard them say this.
What exactly happens when a CT gets shorted? Is it an instantaneous discharge around the coil? And right after it's shorted - it's lost it's potential energy and then harmless?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Shorted CT will still produce voltage evrn shorted but very minimal depending on what the circuit burden is for a given current. Shorted at .1 ohms st 5 amps gives you .5V at the terminls and at 100 amps gives you 50V during faults at max rating.
cheers
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?
Also, I would lose the last set of switched terminals market N, A, B, and C.
I just don't like this design philosophy. There are too many places where a small oversight may result in an open circuit CT.
Note: conventional power faults are the result of a low impedance path causing a high current. Fuses are used to interrupt the fault current.
CT faults are the result of a high impedance path causing a high voltage. A short circuit always makes the secondary of a loaded CT safe. (Assuming a good CT and some faulted CTs also.)
There are a lot of similarities between CT action with an open secondary and a series lighting circuit with an open circuit. A lamp that normally runs on about 50 or 60 Volts may jump to several thousand volts if a lamp fails and the circuit opens. Automatic shorting buttons may be used to short circuit a lamp socket and remove the high voltage. The shorting device also keeps the other lamps in the circuit lit.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Grounding of CT's on a new transformer. Where should the ground connection be located?