Customer tap box connected to secondary spot network

Customer tap box connected to secondary spot network

Customer tap box connected to secondary spot network

(OP)
I am helping a facility out and noticed that they had a secondary spot network with the fault contribution around 75,000A symm. They have a homemade tap box (no ul listing, field fabricated with bus bars with very small standoffs). Does this box need a ul listing and be properly braced for the fault current it could recieve?

RE: Customer tap box connected to secondary spot network

Which side of the meter is it on? It only needs a UL listing if someone makes one with a UL listing. When you start poking around in low voltage network vaults, you'll find lots of scary things.

RE: Customer tap box connected to secondary spot network

(OP)
It is the customers tap box located in their main electric room. It is where the utiltiy and customer meet. I stay very far away from utility vaults!

RE: Customer tap box connected to secondary spot network

If the inspector didn't object, I would say it apparently did not require a UL label at the time it was installed. Is this 208 V? The fault current drops drastically as the distance from the transformer increases. I guess I wouldn't make an issue of it unless this is something you will be modifying. If this was an underrated circuit breaker, I'd approach it differently, but this may not even be a problem.

RE: Customer tap box connected to secondary spot network

(OP)
It is 480V and I am doing a building evaluation and thought this was worth mentioning. My logic for this critical site is if there is a large fault the tap box may explode.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources