Fuel Gas Bolier Tested with N-1 Burner
Hello Everybody:
My Client has requested to test a Fuel Gas Boiler with at least one burner out of operation, and that the remaining burners shall meet 100% of MCR together in that case.
The manufacturer will supply Three Fuel Gas Boilers with 3 burners each one and indicate that test the boilers with 2 burners and meeting 100% of MCR will imply a new design and increase in cost. The Manufacturer indicates since each boiler operate with fuel gas and there will be three boilers operating in paralell, is unnecessary this test because this situation will never occur (one boiler operating with a burner out of operation per maintenance or other situation, however, my client requested it.
What do you think about this?
Can occur that one burner fail and the boiler continue operating with two burners safety?
Eng. Orangel Roca
Venezuela
Eng. Orangel Roca
Venezuela
RE: Fuel Gas Bolier Tested with N-1 Burner
In this scenario to give you something of an answer, I would go with what the manufacturer indicates as proper or safe operating conditions. If the manufacturer indicates that the boiler should not be run without all three burners operating correctly, then your company should not plan on running the boiler with only two. This is no different than with any other product. You can run it outside of the manufacturer specifications but you do so at your own risk.
Doug