2" concrete fill over existing SOG
2

2" concrete fill over existing SOG

2" concrete fill over existing SOG

(OP)
Existing construction with 5" concrete slab on grade with 2" mud-set tile. The mud set tiles were removed for a portion of the new slab due to some new work and the question now is how to infill back the 2" with new concrete. To me it appears that the 2" is similar to non-structural topping over precast planks. I don't see any issues with providing such a thin topping granted we specify welded wire mesh and control joints at 15' max.

Is 2" too thin of a topping over existing slab?

RE: 2" concrete fill over existing SOG

I suggest using a bonded overlay:

1. Scabble or otherwise roughen the entire surface of the existing slab.
2. Carefully clean this roughened surface.
3. Wet-soak the roughen surface for 24 hours.
4. Place the 2" overlay (plain concrete, no wire mesh).
5. Wet cure for 7 days.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: 2" concrete fill over existing SOG

I've personally laid slab overlays varying in depth from 1" to 3" with no problems other than a little shrinkage which I controlled with pour sequence. Just used a ready mix concrete too, nothing special.

Mike McCann
MMC Engineering

RE: 2" concrete fill over existing SOG

(OP)
Slide, thanks for the input. How do you control shrinkage cracks?

RE: 2" concrete fill over existing SOG

Match the joints and cracks in the existing slab. Since the overlay is only 2" thick AND is bonded to the underlying slab it should actually become a part of the underlying slab. The bond between roughen, cleaned and thoroughly moistened concrete (underlying slab) and the new concrete (the 2" overlay, properly wet cured) is considered by some authorities to be as good as, or better, than an epoxy bond.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: 2" concrete fill over existing SOG

I agree with SRE, but you still may get some restraint shrinkage cracking. Why is that a problem?

RE: 2" concrete fill over existing SOG

Agree with SRE.....bonded overlay, matched joints. As hokie66 says, you'll probably still get some shrinkage cracks. Try to keep the coarse aggregate size as large as possible for the overlay and make the strength of the overlay consistent with the strength of the substrate...meaning the overlay should be weaker at time of placement than the substrate's present strength, but gain strength with time to more closely match existing. This helps to keep differential shrinkage down.

Wet curing is a necessity for a bonded overlay, in my opinion.

RE: 2" concrete fill over existing SOG

(OP)
Thank you all.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources