Contribution from Utility Distribution Load for 3-phase and 1-phase-Ground faults

Contribution from Utility Distribution Load for 3-phase and 1-phase-Ground faults

Contribution from Utility Distribution Load for 3-phase and 1-phase-Ground faults

(OP)
Hi All,

I am involved in accepting connections of new generators on our LV, 11kV and 33kV distribution network. Most of new generators are either CHP (gas engine) that will run Long Term parallel with utility (or) Diesel Generators (DG) that will run parallel only for short duration (1 min typical). Typical generator size range from 0.5MW to 5MW.

We are reviewing our acceptance criteria for new generators and hence want to hear from you guys. The question is regarding 33 or 11kV fault levels at out primary substation (mainly 132/11kV or 132/33kV) bars and to assess break/ make capability of breakers.

At present, we include the load contribution as 1.1 x maximum demand on the bus bars for both the break as well as make conditions. I believe this comes from G-74 (UK standard).

I want to know what load contribution we should add in our break and make analysis? Please note that in our distribution network the load is mixed commercial/ residential loads which do not include large industrial loads.

musa UKPN

RE: Contribution from Utility Distribution Load for 3-phase and 1-phase-Ground faults

Hi Musa

The contribution from distribution will be mainly by Motors . it equals 4 x Nominal Current .
also you should consider the asymmetric factor for total load .
I sc_asym = K * I sc_sym ; K = 1 to 2 ; practically it can be considered = 1.7 max ;

Fault Current = K * Isc_sym + 4 * I_motor .

thanks

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources