Loher Motor... Ex?

Loher Motor... Ex?

Loher Motor... Ex?

(OP)
I have to find out if a motor is Ex proof. But I cannot find a Datasheet. The motor is a Loher ENGV132MB-42. On the plate there is a marking saying: E Exe II. Can someone confirm or guide me to the manufacturer datasheet to verify if this is a Ex Proof unit?

RE: Loher Motor... Ex?

(OP)
Thanks. It seems Loher motor is a Type of motor manufactured or at least sold by Siemens nowadays. Thanks.

RE: Loher Motor... Ex?

(OP)
Thanks. I just read the forum policies. I have downloaded the loher information which I am reading right now. I definitely need to polish up my google kung-fu. I spent several hours looking for info without finding such a useful info. Thanks again. I kinda get interested in the other threads your posted or answered. Impresive long list. I am checking them now.

RE: Loher Motor... Ex?

Since "explosionproof” is typically an NEC, “Division” term, I will tell you that, if the only mark on the motor is E Exe II, it is not explosionproof.

While DRWeig is correct saying “Ex d” is closer, it still isn’t explosionproof; it is IEC “flameproof”. While they are similar in concept, they use different test standards.

The mark as you indicated appears to be ATEX. The first “E” means it is marked for (EU) Zones. The Ex e is “increased safety” suitable for Zones 1 and 2 and the “II” alone is means suitable for all gas and vapor Groups.

In the US, “Ex-anything” is meaningless; it must be AEx. See NEC Section 505.9(C)(2)(3). Again the US domestic test standards are different.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources