sub station earthing

sub station earthing

sub station earthing

(OP)
To all

i have a situiation within a REC switchroom ,housing HV/LV equipment.The REC has requested2 No. earth pockets (normal)However,the main contractor has tried to install 2 No.Sealed earth electrode unsuccessfully.They have asked whether or not they could use the rebars as the earth path and install a fly lead to a dedicated earth bar; My question would be has this to be an isolated connection, they is an lightinging protection scheme currently in place that also uses the re-bars in one or two places.

Your swift reponses would be appreciatied, prior to me contacting the REC.

Thanks in advance.

XXXXXx

RE: sub station earthing

See thread 238-34469 on UFER grounding.  It may help in your request.

RE: sub station earthing


It is likely IEEE 80-2000 Guide for Safety in AC Substation Grounding would be applicable.  
  

RE: sub station earthing

Suggestion: Following up on Busbar applicable IEEE 80-2000.
Normally, there would be an undeground grounding mesh that should be used for the equipment grounding, touch voltages evaluation, step voltages evaluation, etc. If it is not there, then there will be the need for eleborate grounding to substitute the ground mesh.
The lighting protection may have separate ground rods. See NFPA 780 or its equivalent.
http://www.nfpa.org/catalog/product.asp?pid=78000&src=nfpa

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources