Definition of secondary members
I am working on a steel box truss for an overhead sign structure. I am using the AASHTO "LTS-3" design code along with the AASHTO Standard Specs for Highway Bridges, since this is an ASD design (lucky me). I am also referring to the AISC code.
My question is about the connection for web angles bolted to gusset plates, which are welded to a tubular chord member. The AASHTO Std code §10.24.1.6 states "Bolted bearing-type connections ... shall be limited to members in compression and secondary members."
Can webs be considered as secondary members in a truss? I cannot find any solid definitions regarding "secondary members" in the AISC or AASHTO Std codes. The AASHTO LTS-3 code mentions it once in §1.9.2 .
The peak loads are about 50 kips tensile force, and the 'standard' design calls for only two bolts per web. As a result, I will require 1-3/8" A325 bolts if limited to friction-type connections. As the design requires 5x5x½ angles, this violates AASHTO Std code §10.24.4.2, requiring the fastener diametre to be 25% or less of the leg width.
Thanks for you input!
RE: Definition of secondary members
Primary member: Takes calculated stresses - on the load path of your structure.
Secondary member: Does not take calculated stresses on the load paths, but simply provides bracing to the primary members to keep the primary members from buckling.
Secondary members as you are probably aware can be connected with bearing type connections. This should ease your 1-3/8" bolt issue.
This confirms my thoughts that the webs are essentially holding the chords apart, and are indeed secondary members.