Thermal Analysis of Electrical box
I am a mechanical engineer (not the strongest thermo background) and have been tasked with solving a heat transfer problem. I have a junction box with electrical devices inside that produce 30W of heat. The box's surface area is 0.26m. The box is made out of steel. The ambient temperature is 35C. The electrical devices are near the bottom of the box and I want to find the surface temperature of the box.
Correct me if I am wrong, but I am right to neglect radiation in this instance. Also, would a resistance network be the best route to solve this problem since radiation is neglected?
Any help would be great!
Mike
Mike
RE: Thermal Analysis of Electrical box
That would depend on the area of the devices, but, in general, you ought not ignore radiation, particularly in a enclosed space. You've not given sufficient information about the size of the heat source, so the interior temperature might be extremely toasty, literally.
TTFN
Now, your problem will be setting the boundary conditions. Will your box be next to a smelting furnace, or will it be outside at Vostok Station in Antarctica? You'll have to make some assumptions or else run the analysis many times. That's pretty easy to do, though.
It'll do your finite-element or resistance-network thing for you, and it accounts for internal radiation between members that have calculated or defined surfaces. It'll give you two planes of analysis, which should be plenty. If concerned, or if your box is assymetrical, spin it 90 degrees and solve it again, then mesh your results.
http://windows.lbl.gov/software/therm/therm.html Get the architectural materials database with it. You can then easily model example walls to which your box might be mounted. The architectural package also has a better array of metals in it. Don't forget the manual.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
I will check out the software! Thanks for the tip. The boundary conditions are such that it will in a climate/room that will be roughly 35C and mounted on a wall.
IRstuff:
"in general, you ought not ignore radiation, particularly in a enclosed space."
Why is this? Wouldn't it be mainly convective inside of this box?
Mike
TTFN
So I can assume these electrical devices will be radiating power since the box is enclosed? I think I have enough information to get me going.
Best to you,
Goober Dave
Your box is a kind of small and inexpensive. I would build one up and measure the surface temperatures - either to verify my calculations or as a substitute for calculating. 35°C ambient shouldn't be too hard to produce. If it is, run your test at 25°C measure temperature rise over ambient. It'll be close to the same, as long as your 30W load stays constant.
Best to you,
Goober Dave
I've had a bit of a play with THERM and with the libraries you mention. One question I have, and perhaps it will reveal a greater misunderstanding, is how do you model the heat source? Or is the idea not to enclosure your model and instead model just one half and take for example, the left as outside and the right as inside?
Any further resources on applying therm to electronics enclosures that you know of?
I tend to use the half-n-half method you described for pieces that are fairly symmetrical, with single heat sources or at least grouped heat sources.
For stranger things, I'll put little convoluted dents in the side of the panel on which the heat sources will mount.
OK, I just typed a page of description of the two methods I use. I promptly deleted them after proofreading in preview mode. I need pictures! I'll dig out a couple projects and post them later (might be a couple days) with some annotation.
Best to you,
Goober Dave