Can wooden fence be used as a temp. Fence on portion of a substation?
Do we have to follow all grounding rules if a metal fence is used?
Thanks
Do we have to follow all grounding rules if a metal fence is used?
Thanks






RE: Substation temp. Fence
If the fence is partially inside and partially outside the substation ground grid then, although it may be metal, there must be an insulated section (not metal!) at the boundary of the ground grid to separate the sections of fence inside and outside the ground grid. The area inside the substation is tied to the ground grid, the area outside is not.