Low Delta T Syndrome

Low Delta T Syndrome

Low Delta T Syndrome

(OP)
What is the easiest fix for the Low Delta T syndrome in a typical primary/secondary chiller plant set up.

Reading in one of the ASHRAE Journals it was suggested to control chiller from the secondary supply water temperature rather than from the primary, if the supply water in the secondary is gettting higher than the maximum allowed temperature for 5 minutes then start another chiller. This might make sense since the DDC system will not see low delta T on the primary and start another chiller when the first chiller is not loaded 100% .

Opinions?

RE: Low Delta T Syndrome

When you say "low delta T" I assume by this you mean that you are getting poor (low) return temperatures. More often than not, this is a problem at the building level and can be caused by several factors such as stuck valves, dirty or broken air handler coils, etc and too often the default (and incorrect) response is a call for more chilled water. Having poor return temperatures will cause your production to run inefficiently resulting in running extra chillers, which sounds like your trying to avoid.

At our facility, we use two different control methods, depending on the situation (time of year and other factors). One method we use is based upon differential pressure, which is an indication of load. The second method, which sounds a lot like what your considering we call "load factor", which is in essence a calculation of percent of full load. Under this method, we won't start another chiller until both the current "load factor" is at 110% AND the supply water temperature is above a threshold.

RE: Low Delta T Syndrome

(OP)
Controlling it with dP is not an option in our case since the engineer that designed one of the buildings on our campus didnt provide tertiary pumps and we are using secondary pumps to lift the water to the highest level of the building and we can't go below certain dP settings on the system which is to high. Adding tertiary pumps in this building would be a possible solution but we would like to try least expensive things first.
When you say calculating percent of full load I assume that you mean chiller load. Correct?

RE: Low Delta T Syndrome

Gogisha,

Sounds like a perfect place for pressure-independent control valves.

RE: Low Delta T Syndrome

Quote:

When you say calculating percent of full load I assume that you mean chiller load. Correct?
Yes, calculated chiller load. Note, that this doesn't necessarily mean the machines full load by the manufacturer's standards. For example, we've found that some of our constant speed machines run much more efficiently in terms of kw/ton when "maxed" at about 85% full load capacity. Hence, for control purposes in determining when to bring a second machine on line, we could calculate the 'load factor' relative to this reduce capacity value.

Quote:

our campus didnt provide tertiary pumps and we are using secondary pumps to lift the water to the highest level of the building
I understand what you are saying. Also keep in mind that there is a difference between static (head) pressure and differential pressure, the former being controlled by your water makeup and the latter being a function of pump speed (flow). The ability to deliver water to the highest building will be a function of head, which is a function of both the pump head and the head (pressure) at the suction side which is influenced by the make up system.

RE: Low Delta T Syndrome

Some really good relevant work on this subject by Gil Avery (Fellow, ASHRAE):

http://files.engineering.com/getfile.aspx?folder=7...

http://files.engineering.com/getfile.aspx?folder=e...

http://www.achrnews.com/articles/print/get-the-mos...


If you investigate btrueblood's suggestion, be cautious of the extra pump head needed to keep the pressure-independent valves in their control range. They can work well if designed in from the start (though I'm not a big fan of them, energy-wise). In retrofit of an existing system, you need to make sure that your existing pumps and piping can produce the head needed at the control valve location.

I think you'll find your answers in Gil's papers above.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Low Delta T Syndrome

As a first step why not calibrate all temperature sensors and set them to design temperatures.Also have all coils cleaned.That will go a long way in reducing chilled water demand.

RE: Low Delta T Syndrome

Good first steps, SAK9. If the system once worked, it should work again. Look for failed (or disconnected) chilled water valve actuators, cranked-open balancing valves, and other quick-fixes that may have been performed by staff.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources