Temporary Work Pad Requirements

Temporary Work Pad Requirements

Temporary Work Pad Requirements

(OP)
The customer has offered to level ground and pour a temporary work pad (200 ft X 200ft) for the tank erector to fabricate tanks, that will be placed on final foundations after fabrication.

No subgrade study has been performed. Loads are expected to be less than 1000 psf. Is it enough to simply recommend scarification and compaction of top 12" layer , and then recommend a pad thickness with minimum steel?

RE: Temporary Work Pad Requirements

For sure, do something, don't just assume that the soil is ok. If you proof roll the entire existing surface with a loaded dump truck and find no soft spots your proposal should be adequate... but soil testing would be better.

Also, assuming the final foundations are nearby, take a look at soil test results for that location to get a general idea of conditions.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: Temporary Work Pad Requirements

Loaded dump truck is ideal compactor. If you want to have a rule for more improvement, set a limit for rut depth at say 2" max, or 1" if you are real fussy.

Why any steel? Makes removal easier. I'd assume there will be planking under the tank and cranes to spread loads some. Expect cracking from shrinkage.

RE: Temporary Work Pad Requirements

(OP)
Thanks for the comments. Would control joints be a worth while recommendation? Or, just an unnecessary cost?

RE: Temporary Work Pad Requirements

For a 200' x 200' slab with minimum reinforcement, yes, if you don't have enough construction joints. Don't continue the rebar through the construction joints. If you do have control joints, in addition to construction joints, don't run the rebar through them either. You want to do everything possible to make sure that cracks occur where you want them to be... at the control joints. IMHO, don't skimp on concrete thickness, you will be relying on aggregate interlock at cracks / joints to minimize differential settlement.

Having unreinforced joints will make this temporary slab easier to remove later.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources