paint booth classification
paint booth classification
(OP)
at our shop we have a paint booth, we want to put a lift table in it from what iam getting out of the nec book 500-7,
516-2, 516-3 the table would have to be a class I, Div I rated lift table and the conduit would have to be rigid am i correct.
the booth is made of concrete block, has and open front, slot in top for overhead crane chain, and exhuast at the back.
516-2, 516-3 the table would have to be a class I, Div I rated lift table and the conduit would have to be rigid am i correct.
the booth is made of concrete block, has and open front, slot in top for overhead crane chain, and exhuast at the back.





RE: paint booth classification
Interms of a lift table, some tables are hydralic and use either air controls or intrinsic saftey controls.
This would require the pump motor and lift ramps being connected thru hydralic hoses. (motors can be located in an unclassied area reducing costs)
Some paints will not tolerate any contamintes (even vapours of personal anti deodorants can reck the finish) and so a hydralic lift table would not be the answer.
If the lift table has have the electrical motors within the booth area. electrical connections can be made with either ridgit conduit or explosion proof cables and glands appoved for the area. And all the components within the lift table would have to be approved for the area classification.
RE: paint booth classification