Solution pump Error and cooling water Pipe size
Solution pump Error and cooling water Pipe size
(OP)
Is there any relation between Solution Pump and cooling water pipe size?
I have installed pipe of 8" for flow of 2337 gpm at condenser water side, the pump which i have used has enough head to cop up the pressure drop, the chiller operated at full load for about 5 months but now when atmospheric temperature is at peak, the chiller is giving an alarm of solution pump error, is this alarm has anything to do with condensing water flow or pressure drop??? or this might be malfunctioning of electronic parts of the machine (the chiller is single effect double lift hot water absorption machine)
I have installed pipe of 8" for flow of 2337 gpm at condenser water side, the pump which i have used has enough head to cop up the pressure drop, the chiller operated at full load for about 5 months but now when atmospheric temperature is at peak, the chiller is giving an alarm of solution pump error, is this alarm has anything to do with condensing water flow or pressure drop??? or this might be malfunctioning of electronic parts of the machine (the chiller is single effect double lift hot water absorption machine)





RE: Solution pump Error and cooling water Pipe size
Have you checked the capacity of the heat rejector?
Have you contacted the absorption machine manufacturer?
RE: Solution pump Error and cooling water Pipe size
I think he is juct putting the blam on my side by saying that you have used 8" pipe for condensiong water side which is causing pressure drop and thats why chiller is giving this sort of alram, capacity of chiller is 400TR and load on chiller is 80% that is about 320TR AHUs are installed on it
RE: Solution pump Error and cooling water Pipe size