differential relay slope setting.

differential relay slope setting.

differential relay slope setting.

(OP)
hello engineers, from the differential relay manual, they recommended the setting for 1st bias slope setting is 1x tap change range. my transformer got 5 tap and range is 2.5% per tap. so total range is 5% from center.so can i set 0.05 setting for 1st bias slope.

RE: differential relay slope setting.

Who is the differential relay manufacturer?

RE: differential relay slope setting.

You should also include an allowance for CT errors.

RE: differential relay slope setting.

These sound like fixed taps. Do you change taps often? If yes and no, I would use the fixed tap ratio in your tap setting calcs to keep the slope down. If they change frequently, go for a higher slope to avoid frequent protection setting changes. Slope also accommodates CT error as stated above.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources