6ö MOV and gate valve fitting to fitting.

6ö MOV and gate valve fitting to fitting.

6ö MOV and gate valve fitting to fitting.

(OP)



I have a client who wants to install a 6” MOV and a gate valve fitting to fitting on a gasoline storage tank suction line. Is that could practice? Should there be a spool in between with a drain so when the tank is isolated (gate valve) the spool could be drained and the MOV could be replaced/repaired if required?

RE: 6ö MOV and gate valve fitting to fitting.

What happens if the gate valve needs to be repaired. The number of valves in the line doesn't matter. If the wrong one fails, you still need to drain the tank.

An open/close MOV won't require any more maintenance on fluid containing parts than any other valve and the Motor can be repaired without draining the tank.

Independent events are seldomly independent.

RE: 6ö MOV and gate valve fitting to fitting.

The thing that would concern me is thermal expansion of the gasoline between two closed valves if closed on a cool day, but subject to heating could develop really quite high pressures. Whilst the volumes may be small and only need a small amount to leak, you can damage valve seats due to this and gasoline is one of the higher thermal expansion liquid hydrocarbons.

A spool is often useful to provide a support for these quite weighty valves and avoid propping the valve body itself. You can then also put in a thermal relief line draining into a drain or back into the tank.

Otherwise I agree with BI, the fact you're bolted to the isolation should make no difference as to whether you can take the MOV off. All yuo would need to do is hve a small drain pot when you crack the bolts - not too clever, but you're only doing this every few years. A spool would be better but you could find your drain valve seized closed due to inaction....

My motto: Learn something new every day

Also: There's usually a good reason why everyone does it that way

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources