Hi, I'm checking some formulas for Kv and I've seen different formulas.

I use Norgren and ASCO formulas for pneumatic Kv value:
Kv = (Q/514) · sqrt(T1/(Dp·p2))

Now the ISA control valve handbook is:
Kv = (Q/(482·Y))·srqt(T1·Z/(Dp·p1))

So, if Y and Z are approximately 1 for air this is:
Kv = (Q/(482))·srqt(T1/(Dp·p1))

How is it that one is sqrt(T1/(Dp·p1)) and the other sqrt(T1/(Dp·p2))
Maybe I shouldn't use ISA formulas for pneumatic valves, but should't they be the same?

Regards,

RE: ISA control valves Kv vs Pneumatic Kv

If the lower one is for liquids (and there is nothing to indicate that it isn't), then of course it would be different than the one for pneumatics.

Want to know the do's and don'ts of Eng-Tips? Read FAQ731-376: Eng-Tips.com Forum Policies.
English not your native language? Looking for some help in getting your question across to others or understanding their answers? Go to forum1529: Translation Assistance for Engineers.

RE: ISA control valves Kv vs Pneumatic Kv

(OP)
Hi, the ISA formula is for compressible fluids in non-choked turbulent flows.
ISA-75.01.01-2007 (IEC 60534-2-1 Mod)

Regards,

RE: ISA control valves Kv vs Pneumatic Kv

Ok. I did some searching. I found the ISA reference first and confirmed that the formulas there do reference the inlet pressure. However, none of them set Y equal to 1 and none give the numerical constant that you state. With a little more searching I found a paper from ASCO where, provided that the outlet pressure is greater than or equal to half the inlet pressure, it gives the formula you state. I have to presume that case fits your situation. I was unable to track down the Norgren paper, but I'll take your word that it states the same as the ASCO paper.

My two cents is that any of the formulas would work if they were applied properly. Go with which ever you want to use. However, if you're designing valves, I recommend that you consider testing them to confirm that your actual Kv meets your stated Kv.

Want to know the do's and don'ts of Eng-Tips? Read FAQ731-376: Eng-Tips.com Forum Policies.
English not your native language? Looking for some help in getting your question across to others or understanding their answers? Go to forum1529: Translation Assistance for Engineers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources