Same 87T for 2 transformer not paralleled

Same 87T for 2 transformer not paralleled

Same 87T for 2 transformer not paralleled

(OP)
the transformer auxiliary service of a hydroelectric power plant 13.8/0.44kV-3.5MVA, Delta / star grounded was protected by a 87 as main protection. Later was added another transformer 13.8/13.8kV-6.5MVA, Delta / star grounded using the same 87.
13.8kV delta sides are connected at same source power.Star grounded sides are connected at separated loads. All CTs were appropriate ratio.
What would be the recommendations for 87 operate correctly?

RE: Same 87T for 2 transformer not paralleled

There should be a separate 87T for each transformer, in principle, that trips the HV and LV breakers for its own transformer only and not the other one. This assumes that there is actually a breaker on the HV side of each transformer that can be tripped. If you have fuses only on he HV side or only one breaker for both transformers, then this will not work.

rasevskii

RE: Same 87T for 2 transformer not paralleled

(OP)
I have breaker at each terminal of transformer.
I was worrying about inrush. I guess to energize transformers sequentially with a little delay. Will be this necessary?

RE: Same 87T for 2 transformer not paralleled

odlanor,

If yours is a numerical relay, the second energisation, ergo the inrush current that follows the second energisation should be restrained by the internal algorithm of the differential function block in the relay. So, even if you energise the two transformers sequentially, it shouldn't be a problem.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources