Cooling Tower Area Paint System

Cooling Tower Area Paint System

(OP)
Dear All,

We are observing extensive atmospheric corrosion on piping & structure adjacent to our cooling towers. Most of the piping and structure is of carbon steel in the area. Extensive corrosion is indicating that currently employed paint system is inadequate for this environment i.e. high moisture & humidity. Currently employed paint system consists of :

Epoxy Zinc Phosphate - Primer
High Build Epoxy - Intermediate
Acrylic Urethane - Top Coat

Based on your expereince please evaluate above shared paint system's adequacy as well and also recommend any improvements that can be made in this system.

Regards

RE: Cooling Tower Area Paint System

Hi,
Is this structures where painted under Painting Inspector supervision?
Have you got any info regarding to treated surface, their profile, conditions during painting etc?
Extensive corrosion in your case it may not be connected with wrong painting system but with conditions at which paint was applied.
First you should refer to corrosion protection report if there is.

Regards

RE: Cooling Tower Area Paint System

(OP)
These piping and structure were commissioned in 1998 by a reputed Construction Company i.e. Foster Wheeler. So while there is no such report available to indicate quality of surface preparation, rest of our plant areas painted under same company's supervision are fine indicating good engineering practices were adhered to.

Over the coarse of 15 years areas of paint blisters location were properly cleaned followed by paint application, however since the environment in this area is extremely aggressive we are looking for a paint system that can last much longer. Any suggestions would be much appreciated.

Regards

RE: Cooling Tower Area Paint System

Hi,
It's hard to advise any painting system via internet.
That's fine if the rest of painting system with-stand 15 years. I though it's on new building. To be honest I will not to expect in this aggressive areas any improvements due to humidity/ moisture. What you might change is intermediate to epoxy with MIO e.g. MIO flakes possess very good barrier properties, they are impermeable to water.

http://www.jotun.com/jotun/paints/20020020.nsf/wvw...

it's compatible with rich zinc coatings. 1st coat in your case
But min temp. of substrate during application has to be 15*C.

Regards

RE: Cooling Tower Area Paint System

(OP)
I have applied Jotun Paint's JOTAMASTIC 87 along with HARDTOP XP on experimental basis in the area, we will see its adequacy in months to come.

RE: Cooling Tower Area Paint System

Sounds like a good experiment.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close