Are fuses and/or breakers still required?

Are fuses and/or breakers still required?

Are fuses and/or breakers still required?

(OP)
AB makes claim that these combination starters

http://www.ab.com/industrialcontrols/products/motor_contacters_starters/compact_combination/index.html
proviede:
-Suitable as motor disconnect per UL508 and isolator per IEC 947-2
-Short circuit protection per UL508 Type E and IEC 947-4
-Short-circuit rating up to 100 kA
-Provides short-circuit protection with magnetic trip at 13x the maximum current adjustment range.........

Would you agree that for a small control panel with
 - 10-12 individual motor circuits say few HP
 - and a single main breaker/disconnect - say 200A
no fuses or breaker protection is required for the individual circuits.?

RE: Are fuses and/or breakers still required?

Hello Ares,

Use of these devices as described needs to be in compliance with your local electrical code.  If the code allows usage without fuses or breakers then fine.

I would use them without any fuses or breakers in the individual motor 3-phase circuits.  You would still need a circuit breaker or fuse for the control circuit.  They look to be a good product.  I use the equivalent product from Moeller for smaller motors in panel boards just as you describe.  I also use them in MCC's sometimes.  You can put a whole bunch of them in a tier.  Very space efficient and cost effective.

Regards

   

RE: Are fuses and/or breakers still required?

Suggestion: Please, notice that the starters have protective features integrated; therefore, there is no need for additional external fuses or breakers.
Comment marked ///\\\
Would you agree that for a small control panel with
 - 10-12 individual motor circuits say few HP
 - and a single main breaker/disconnect - say 200A
no fuses or breaker protection is required for the individual circuits.?
///Yes, it is possible, if all protective features are embedded in the individual starters. Compare this integrated technology with integrated protective relays that have many ANSI device number functions integrated in one relay, physically. If the protective ANSI device number is not needed, then it is not used; however, it cannot be removed from the product since it is integrated physically.\\\

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources