How to calculate the extended end plate connection with large axial loads?
How to calculate the extended end plate connection with large axial loads?
(OP)
I have a question about beam extended end plate connection. I designed the beam connection with extended end plate (extended 1" at top and bottom flanges). For the geometry reason, there are no bolts beyond beam flanges (see attachment). I distributed the axial loads according the flange and web cross-sectional area. Is the method right? And where can I find the theory in manual or guides? Please suggestion. Thanks





RE: How to calculate the extended end plate connection with large axial loads?
If that doesn't provide sufficient information, then you can check out the reference papers for the design guide (primarily the ones where Tom Murray is one of the authors). They should go into more depth about the yield line theory methodology used to develop the procedure in the design guide. My belief is your yield lines will be identical to one of the flush end plate connections and that you would therefore, be able to use those equations directly.
RE: How to calculate the extended end plate connection with large axial loads?
Thank you for your explain. In the flush moment end plate or extended end plate moment connection, the axial loads and moment will be resist by beam flanges, not beam web. My concern is if the beam web can resist part axial loads (distributed by section area) or not. If the beam web can resist part axial loads, are there some limitations for the load path (bolts, end plate, etc.)? Thanks
RE: How to calculate the extended end plate connection with large axial loads?
However, I believe you would also want to ensure that the web weld strength is sufficient to develop the strength of the web. I recall seeing that either in AISC358 or one of the End Plate design guides. That way, you are assured that the web will yield before the weld fractures. But, assuming that the tension force goes through the flanges should still be a conservative assumption. I know that is discussed somewhere in the one of the design guides.
RE: How to calculate the extended end plate connection with large axial loads?
Thanks.I still have two questions about the end plate connection.
1. For the flush moment end plate, how can the axial load and moment transfer to beam flange? My Our customer thought there has a question about load path for this design. They thought the axial load can be transferred to column through beam flanges only if the strength of first row bolts are greater than flange force. If not, the axial loads can't transfer to column.
2. I know it is more conservative concern that all tension force goes through beam flanges. But can distributed the tension force by web and flanges section area?
RE: How to calculate the extended end plate connection with large axial loads?
The main difference when you add in axial force is just that you come up with an equivalent moment:
Meq = M + P*d/2
RE: How to calculate the extended end plate connection with large axial loads?
Does the axial load exceed the tensile strength of the beam web? By how much?
Why connect the beam flanges to the end plate for an axial load only?
You can make the end plate extremely thick, but what about the column flange?
www.FerrellEngineering.com