Duct Sizing

Duct Sizing

Duct Sizing

(OP)
I need to relocate the suction air filters for 2 7500 acfm blowers due to high particulate loading.  The thought would be to use some existing 28" diam. duct which is available and move the filtering point about 60' away (we would also have 4 90 degree elbows) from the existing location of the blowers.  Any tips on where to find estimated pressure losses for this flow in 28" diam. duct?  The flow would be 7500 acfm in each duct.

RE: Duct Sizing

For 7,500 cfm and 28" dia duct, the friction factor works out to 0.14" per 100 ft of duct. calculate equivalent length for the elbows and then use this friction factor to determine friction loss.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources