Grounding on Offshore Metallic structure
Grounding on Offshore Metallic structure
(OP)
Hi,
On a fixed offshore oil & gas structure which is completely metallic, Is there any need for a common bonding network, if each equipment is bonded to the metallic structure by cad weld.
Thanks in advance.
Regards
Jay
On a fixed offshore oil & gas structure which is completely metallic, Is there any need for a common bonding network, if each equipment is bonded to the metallic structure by cad weld.
Thanks in advance.
Regards
Jay






RE: Grounding on Offshore Metallic structure
According to IEC60079-14 §6.3 all exposed and extraneous conductive parts shall be connected to the equipotential bonding system which is normally the steel structure.
It is however not required to use seperate conductors if the parts are firmly secured and in conductive contact whith the equipotential bonding system which is the case with a welded connections.
Best Regards
Preben
RE: Grounding on Offshore Metallic structure
thanks alot for the quick reply on the above query.
regards
jay