We have a lube oil unit. we have two separate temperature switches. One of the switches will inhibit the machine start if the temperature is less than 10'C. The other will switch on the oil heaters when the temperature is less than 10 and switch the heaters off when the temperature is equal to 20'C. My question is does this second switch require 2 set points?
Thanks
Thanks





RE: Switch set points
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Switch set points
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
RE: Switch set points
You also need the heaters to be on until the oil temp gets far enough above 10*C that the inhibit switch will reliably work.
The inhibit operation switch will need a dead band of some sort as well.