Hello,

I have a cooking appliance that burns JP-8 fuel in a confined space. It has a forced ventilation hood and makeup air sized with IMC. Can I use the makeup air for the hood to provide combustion air, or do I need to provide a passive opening sized with NFPA 54?

Best

RE: Calculating combustion air for kerosene based fuel burner

The amount of combustion air will depend on the rating of the cooking appliance. Any good ME handbook such as Kent"Power" will have a section on combustion air for different fuels including diesel fuel which in essence is what JP-8 is. Combustion air from such books will be theoretical so you will need to increase that value byI would say 15% or more fora complete combustion of the fuel. Your reference to the hood, is that an exhaust hood over the cooking appliance? and if so, that hood exhausts and does not provide combustion air unless may be you are refering to a "push-pull" system over the appliance. JP-8 fuel is for jets and seems extravagant for a cooking appliance unless you expect it to take off on you,HA,HA and have the stomach for it after you have cooked your food on JP-8 fuel because I would expect some malodours permeating the confined space and possibly the food.

RE: Calculating combustion air for kerosene based fuel burner

Since you got my curiosity peaked, I did some research about the properties of kerosene in my Kent ME and Perry CE handbooks. The kerosene values were for 45 degree API that I used for the attached calculations on an assumed 25,000 btu/hr stove to determine the combustion air requirement. Please see the JPEG attachment.With the stove and JP-8, you may have updated values which you can substitute in the calculations.

RE: Calculating combustion air for kerosene based fuel burner

(OP)
Thanks chicopee!

RE: Calculating combustion air for kerosene based fuel burner

(OP)
After reviewing the Perry handbook I see that the air requirement for kerosene is less that natural gas. I also see that NFPA 54 has a calculation for mechanical combustion air required of 0.35 cfm/1000 BTU. It comes out slightly higher. Since I am using a hood above the appliance I think I need to add a dilution amount too.

RE: Calculating combustion air for kerosene based fuel burner

Don't forget to compensate CFM for increases in altitude and and changes in ambient temperature. Since JP-8 is a military fuel, you are probably stuck in the "boondocks" where conventional cooking fuel may be unavailable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources