Yokogawa UT35A cannot connection using Input current
Sollution
setting Yokogawa UT35A using voltage input,PV Input type 0-10 V.
RH ( v= 330 ohm x 20 mA = 6.6 volt )
RL ( v= 330 ohm x 4 mA =1.32 Vollt )
Yokogawa UT35A cannot connection using Input current
Sollution
setting Yokogawa UT35A using voltage input,PV Input type 0-10 V.
RH ( v= 330 ohm x 20 mA = 6.6 volt )
RL ( v= 330 ohm x 4 mA =1.32 Vollt )