scenario

1. static a fire hydrant
2. go to the next one and flow both 2 1/2's very little drop in pressure
3. sorry no pitot reading, gage gave up. but good flow from both 2 1/2's.

next one, same static fire hydrant

1. fire truck is set on the same static fire hydrant and starts flowing water

2. truck gets around 1800-2000 gpm. intake pressure on truck goes down to around 20 ish psi.

what is going on here?????? why is the truck taking the pressure down so low, versus flowing the 2 1/2's?

RE: fire hydrant flow tests

If I got the idea....

First case. The flow is not that big. And the water source is big and does not suffer a drop on distant "static" hydrant.

Second case. The flow and speed is big. The gage reading sould not be taken on the same hydrant the truck is connected it may suffer from turbulence/venturi effect.

RE: fire hydrant flow tests

(OP)
but with the second scenario, that is real life.

Fire truck pulls up to an fire hydrant, connects , shots the water, and they are told to not drop below 20 psi.

So the 1800 gpm is all the truck can take from the fire hydrant, if they follow the 20 psi rule.

I do follow your thinking though, and thought of staticing another hydrant while the truck pumps, but still they can only get so much water from the hydrant.

RE: fire hydrant flow tests

What may seem a lot of water coming out of hydrant #2 may not be so particularly if Hydrant #2 was at a higher elevation that hydrant #1( your static hydrant).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources