smileHi,
Im trying to comply with the 25% drop in residual\static specified in NFPA 219 when carrying out hydrant flow testing. example below
Remote static 158 psi
hydrant 1 open with residual 154psi and flow 2627 lpm
hydrant 2 open with residual 140psi and total flow (x2 hyds)4735 lpm
hydrant 3 open with residual 116psi and total flow (x3 hyds)6545 lpm
total flow 6545 x (158-20)0.54 / (158-116)0.54 = 6545 x 138 0.54/42 0.54 = 9320 lpm Is this correct?

also
if I had a fire pump with a gauge that showed 170psi and the pump gauge drops whilst opening the hydrants, should I include this in my theoretical calc? if so how?
Thanks for any help

RE: NFPA 219 flow testing hydrants, 25% drop

(OP)
me again!! sorry my theoretical calc should've said 12442 lpm.

RE: NFPA 219 flow testing hydrants, 25% drop

(OP)
can anyone help me?

RE: NFPA 219 flow testing hydrants, 25% drop

Sorry have not done a flow test with a fire pump
On the line and do not know if it is figured in
I think you may have a good representation of the water supply

RE: NFPA 219 flow testing hydrants, 25% drop

4.3.6 To obtain satisfactory test results of theoretical calculation of expected flows or rated capacities, sufficient discharge should be achieved to cause a drop in pressure at the residual hydrant of at least 25 percent, or to flow the total demand necessary for fire-fighting purposes.

""" to flow the total demand necessary for fire-fighting purposes"""""

what is your demand you need??

RE: NFPA 219 flow testing hydrants, 25% drop

(OP)
The area is a storage tank farm so the demand for fighting purposes will easily be exceeded and additional water supplies required!

RE: NFPA 219 flow testing hydrants, 25% drop

The way that I am viewing your numbers is that you have a total of 6545 lpm at a residual pressure of 116 psig taken at the remote static point which I assume is a fourth hydrant; Hydrant flows at 2108 lpm and hydrant 3 flows at 1810 lpm. So plot the remote static value of 158psig and the 6545 lpm at 116 psig on semi-log graph of N=1.85 power to see what lpm at 20 psig the graph shows. I have included an attachment of the graph in question with your values. At 20 psig, 3270 gpm translates to 12376.9 lpm and 3540 gpm translates to 13398.9 lpm.

RE: NFPA 219 flow testing hydrants, 25% drop

That s/b "...Hydrant 2 flows at 2108 lpm and hydrant 3 ......"

RE: NFPA 219 flow testing hydrants, 25% drop

NFPA 291 Recommended Practise for Fire Flow Testing and Marking of Hydrants

Slip of the typing finger, it would appear.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources