Wood Pole Loading Questions

Wood Pole Loading Questions

Wood Pole Loading Questions

(OP)
I have assisted in the writing of a wood pole guy wire and anchor tension calculation program.  The program allows the user to attach wires to a wood pole and attach a guy wire to an anchor and it calculates the guy wire tension plus anchor load.
I have a need to do calculations with loading due to equipment with a moment arm and I believe that I now have a statically indeterminate problem.  Are there methods, other than finite element analysis, that can be used to solve this problem?  The program is written in Excel VBA and uses a hand-calculation approach to calculating tensions.

Any help is appreciated.

RE: Wood Pole Loading Questions

sonar23:  Maybe you could use superposition.  (1) Apply your equipment with moment arm, without the wires attached.  Compute pole transverse deflection at guy wire attachment point due to this applied moment M.  (2) On a separate cantilever, with no wires nor equipment attached, compute applied transverse shear force V at guy wire attachment point required to deflect cantilever the same transverse distance computed in item 1.  This will convert M in item 1 to an equivalent transverse shear load V.  (3) Now solve your original problem, with wires attached (but without moment-inducing equipment attached), except also apply additional transverse shear load V to pole at guy wire attachment point.

The concept above is, convert the applied moment to a simpler force (neglecting the insignificant transverse shear and moment at pole base) to keep the problem statically determinate.  Hope this idea works.  The guy wire tension established in this manner will be slightly conservative if the pole has significant bending stiffness and completely solid rotational constraint at the ground.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources