Current measurement in 11kV screened single core cables using Rogowski coil.
Current measurement in 11kV screened single core cables using Rogowski coil.
(OP)
Anyone able to help?..
Looking to monitor the loadings of a package S/S transformer to add more capacity.
Cannot access the LV small wiring without a shutdown so was proposing moving the open point in order to feed the intended transformer soley from this section of the 11kV ring.
Will this application cause failure to the Rogowski coil?..or even be achievable ..
Looking to monitor the loadings of a package S/S transformer to add more capacity.
Cannot access the LV small wiring without a shutdown so was proposing moving the open point in order to feed the intended transformer soley from this section of the 11kV ring.
Will this application cause failure to the Rogowski coil?..or even be achievable ..






RE: Current measurement in 11kV screened single core cables using Rogowski coil.
As you apparently can not tolerate an outage to install metering equipment, if the screen connections have not already been configured to suit this requirement, primary metering (accurately) will not be possible.