Merlin Gerin Masterpact STR58U
Unfortunately I found this website 3 years to late. In 2010 I had a problem with a 1200 amp unit intermittently tripping. It had an STR28D trip unit. This was part of a emergency transfer system gear normal breaker. Square D had tested the breaker in place and said it was fine. I had run chart recordings on the circuit for over a week and nothing was abnormal. The problem got so bad I had to turn on the generator and run on the emergency breaker until I could do an overnight outage to replace. It too started tripping. Square D and my contractor were involved in replacing the normal breaker (unfortunately it was a bolt in breaker so it took over 10 hours to change out). Total bill for replacement with a spare breaker that I had was over $11,000, plus the bill for recording meter testing and for testing the original breaker off site. I sent out the breaker for testing and everything came back fine.
Just 4 weeks ago I had a 1600 amp breaker in the gear start doing the same thing. It to had the STR28D trip unit. Square D finally admitted there are problems with that trip unit and that unit is obsolete. They recommended replacing the trip unit with an STR58U and that their tech had to do it. It only took 30 minutes and cost over $4500.
I have 5 more breakers with the STR28U trip units in them and requested a quote for replaceing all 5 ($24,000).
After going through this experience, I am looking into buying the trip units from a third party and having my contractor do the replacement (trust me, it's not rocket science to replace).
So buyer beware. After reading these forums, I discovered Schneider/Square D knew about this problem prior to 2000. The gear I have was installed in 2001 just prior to my coming to this company. I consider their practice of installing devices know to be defective and further not admitting it 10 years later when the problems started is less than ethical. Save yourself the agravation and your company the money and make sure you are not getting ripped off.
RE: Merlin Gerin Masterpact STR58U