UK pressure regulations

UK pressure regulations

UK pressure regulations

(OP)
I have a reactor on a chemical plant which does not come under the UK pressure systems regulations as it is not pressurised. However, as it is a multipurpose vessel, it is possible to apply cooling water, glycol or hot water to the jacket. Does anyone know whether the hot water configuration falls within the scope of PSSR? The hot water is pumped at more than 0.5barg, but would not boil on release, so does it qualify as a "relevant fluid"?

RE: UK pressure regulations

If it's over 0.5 Barg then the PED applies!!!

RE: UK pressure regulations

"Vessels designed to contain liquids with a gas pressure above the liquid of not more than 0,5 bar" are exempt from PED (article 1, para 3.21), but pessure systems safety regulations does cover hot water being pumped at above its atmospheric boiling point (UK HSE PSSR approved code of practice) It also talks about accidental pressurisation.

I'd want to be very confident that there's no way of pressurising a gas filled vessel (for example closing an outlet valve on an empty jacket and starting your water pump). There is not enough information in your description to offer advice either way.

In either case you need to be able to robustly document how you've decided that it is in/out of scope, so I'd suggest retaining a suitably qualified/experienced engineer as your 'competent person'.

Matt

RE: UK pressure regulations

(OP)
Thank you. I had come to the conclusion that it was not included but was not confident in the decision. Reminding me to consider accidental pressurisation is most helpful.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources