Hi,
What are good Chiller Leaving/Returning water temperatures for residential applications? I've seen mostly 42°F LCWT. What about dT?
I know that the best temperatures will require a thorough analysis of the entire system including pumps, piping loop design, fan coil cost, pressure drops..etc, on a case to case basis. But as a rule of thumb, what would be some good values?
Also, and sorry for this show of ignorance, what is meant by "10°F water range in the evaporator"? Is this the dT?

Best Regards

RE: Recommended Chiller Leaving/Returning Water Temperatures

The basic chiller specification starts at 42 degF with a dT of 10 degF. Most chillers can be configured to run over a fairly wide range of temperatures, the dT usually stays around 9 - 10 though.

RE: Recommended Chiller Leaving/Returning Water Temperatures

(OP)
Thank you for the response. I understand. Would you be so kind to answer the part about the 10°F water range? I do know that the evaporator is where the chilling of the water takes place, but maybe this refers to something else? The reason I'm wondering is because the terms I've come across are Delta T, or Water Temperature Rise (WTR). I've not come across this term before.

Regards

RE: Recommended Chiller Leaving/Returning Water Temperatures

I believe the temperature range you mention is the delta T. Can't think of anything else it would be. Often times your CWS temp is dependent on your de-humidification loads. If designing from scratch I would optimize coil/chiller selection for the warmest CWS temperature and highest delta T while still meeting latent and sensible loads. Higher CWS temp means less compressor lift and energy savings. Higher delta T means less flow and pumping energy.

RE: Recommended Chiller Leaving/Returning Water Temperatures

(OP)
Thank you for the response.

Regards

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources